27 Electrical Safety & Regulation questions from the Plant & Utility Ops bank, written for Indian campus drives and tech interviews. Every question has a verified answer and an AI-tutor explanation on placd.
Free to start: the 2-minute EE readiness check — six questions and a result.
A.each worker fits a personal lock and tag on every isolation point after switching off and testing for dead, so no one can re-energise the circuit until the last lock is removed
B.isolate, secure against reconnection, verify dead with a tested detector, earth and short-circuit, then screen adjacent live parts, in that order before any work
C.NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance
D.full-body harness with double lanyard anchored above about 1.8 m, ladders at a 4:1 slope, and no work near live overhead lines from ladders or structures without a permit and discharge
Answer + AI explanation with Pro
2. Which term means: "isolate, secure against reconnection, verify dead with a tested detector, earth and short-circuit, then screen adjacent live parts, in that order before any work"?
Junior
A.Arc flash PPE categories
B.Five safety rules
C.Electrical accident reporting
D.Permit-to-work
Answer + AI explanation with Pro
3. Which statement is correct?
Junior
A.Five safety rules — CEA schedule of minimum distances from exposed live parts for work: 2.6 m at 12 kV, 2.8 m at 36 kV, 3.1 m at 72.5 kV, 3.7 m at 145 kV, 4.3 m at 245 kV and 6.4 m at 420 kV
B.Five safety rules — IEC 60479 places the onset of fibrillation near 30–50 mA for a few hundred milliseconds, which is why 30 mA residual-current protection is chosen for personnel
C.Five safety rules — NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance
D.Five safety rules — isolate, secure against reconnection, verify dead with a tested detector, earth and short-circuit, then screen adjacent live parts, in that order before any work
Answer + AI explanation with Pro
4. What is Lockout-tagout?
Junior
A.each worker fits a personal lock and tag on every isolation point after switching off and testing for dead, so no one can re-energise the circuit until the last lock is removed
B.full-body harness with double lanyard anchored above about 1.8 m, ladders at a 4:1 slope, and no work near live overhead lines from ladders or structures without a permit and discharge
C.isolate, secure against reconnection, verify dead with a tested detector, earth and short-circuit, then screen adjacent live parts, in that order before any work
D.CEA Safety Regulations require every fatal or non-fatal electrical accident to be reported to the Electrical Inspector within 48 hours, followed by a detailed written report
Answer + AI explanation with Pro
5. Which term means: "each worker fits a personal lock and tag on every isolation point after switching off and testing for dead, so no one can re-energise the circuit until the last lock is removed"?
Junior
A.Arc flash PPE categories
B.Five safety rules
C.Lockout-tagout
D.Working at height
Answer + AI explanation with Pro
6. Which statement is correct?
Junior
A.Lockout-tagout — Indian recommendations on safety procedures and practices in electrical work, Part 1 general and Part 2 life-saving techniques including rescue and artificial respiration
B.Lockout-tagout — IEC 60479 places the onset of fibrillation near 30–50 mA for a few hundred milliseconds, which is why 30 mA residual-current protection is chosen for personnel
C.Lockout-tagout — each worker fits a personal lock and tag on every isolation point after switching off and testing for dead, so no one can re-energise the circuit until the last lock is removed
D.Lockout-tagout — CEA schedule of minimum distances from exposed live parts for work: 2.6 m at 12 kV, 2.8 m at 36 kV, 3.1 m at 72.5 kV, 3.7 m at 145 kV, 4.3 m at 245 kV and 6.4 m at 420 kV
Answer + AI explanation with Pro
7. What is Permit-to-work?
Mid
A.isolate, secure against reconnection, verify dead with a tested detector, earth and short-circuit, then screen adjacent live parts, in that order before any work
B.formal authorisation by an issuer to a receiver listing the isolations, earths and safe zone, held live until the receiver returns it and the issuer cancels it before re-energisation
C.CEA Safety Regulations require every fatal or non-fatal electrical accident to be reported to the Electrical Inspector within 48 hours, followed by a detailed written report
D.CEA schedule of minimum distances from exposed live parts for work: 2.6 m at 12 kV, 2.8 m at 36 kV, 3.1 m at 72.5 kV, 3.7 m at 145 kV, 4.3 m at 245 kV and 6.4 m at 420 kV
Answer + AI explanation with Pro
8. Which term means: "formal authorisation by an issuer to a receiver listing the isolations, earths and safe zone, held live until the receiver returns it and the issuer cancels it before re-energisation"?
Mid
A.Arc flash PPE categories
B.Permit-to-work
C.IS 5216
D.Five safety rules
Answer + AI explanation with Pro
9. Which statement is correct?
Mid
A.Permit-to-work — formal authorisation by an issuer to a receiver listing the isolations, earths and safe zone, held live until the receiver returns it and the issuer cancels it before re-energisation
B.Permit-to-work — each worker fits a personal lock and tag on every isolation point after switching off and testing for dead, so no one can re-energise the circuit until the last lock is removed
C.Permit-to-work — isolate, secure against reconnection, verify dead with a tested detector, earth and short-circuit, then screen adjacent live parts, in that order before any work
D.Permit-to-work — NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance
Answer + AI explanation with Pro
10. What is Electrical accident reporting?
Mid
A.NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance
B.formal authorisation by an issuer to a receiver listing the isolations, earths and safe zone, held live until the receiver returns it and the issuer cancels it before re-energisation
C.isolate, secure against reconnection, verify dead with a tested detector, earth and short-circuit, then screen adjacent live parts, in that order before any work
D.CEA Safety Regulations require every fatal or non-fatal electrical accident to be reported to the Electrical Inspector within 48 hours, followed by a detailed written report
Answer + AI explanation with Pro
11. Which term means: "CEA Safety Regulations require every fatal or non-fatal electrical accident to be reported to the Electrical Inspector within 48 hours, followed by a detailed written report"?
Mid
A.Lockout-tagout
B.Ventricular fibrillation threshold
C.Electrical accident reporting
D.Working at height
Answer + AI explanation with Pro
12. Which statement is correct?
Mid
A.Electrical accident reporting — CEA Safety Regulations require every fatal or non-fatal electrical accident to be reported to the Electrical Inspector within 48 hours, followed by a detailed written report
B.Electrical accident reporting — formal authorisation by an issuer to a receiver listing the isolations, earths and safe zone, held live until the receiver returns it and the issuer cancels it before re-energisation
C.Electrical accident reporting — CEA schedule of minimum distances from exposed live parts for work: 2.6 m at 12 kV, 2.8 m at 36 kV, 3.1 m at 72.5 kV, 3.7 m at 145 kV, 4.3 m at 245 kV and 6.4 m at 420 kV
D.Electrical accident reporting — NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance
Answer + AI explanation with Pro
13. What is Arc flash PPE categories?
Senior
A.isolate, secure against reconnection, verify dead with a tested detector, earth and short-circuit, then screen adjacent live parts, in that order before any work
B.each worker fits a personal lock and tag on every isolation point after switching off and testing for dead, so no one can re-energise the circuit until the last lock is removed
C.Indian recommendations on safety procedures and practices in electrical work, Part 1 general and Part 2 life-saving techniques including rescue and artificial respiration
D.NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance
Answer + AI explanation with Pro
14. Which term means: "NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance"?
Senior
A.Five safety rules
B.Arc flash PPE categories
C.Safety working clearance
D.Ventricular fibrillation threshold
Answer + AI explanation with Pro
15. Which statement is correct?
Senior
A.Arc flash PPE categories — Indian recommendations on safety procedures and practices in electrical work, Part 1 general and Part 2 life-saving techniques including rescue and artificial respiration
B.Arc flash PPE categories — NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance
C.Arc flash PPE categories — IEC 60479 places the onset of fibrillation near 30–50 mA for a few hundred milliseconds, which is why 30 mA residual-current protection is chosen for personnel
D.Arc flash PPE categories — isolate, secure against reconnection, verify dead with a tested detector, earth and short-circuit, then screen adjacent live parts, in that order before any work
Answer + AI explanation with Pro
16. What is IS 5216?
Junior
A.Indian recommendations on safety procedures and practices in electrical work, Part 1 general and Part 2 life-saving techniques including rescue and artificial respiration
B.each worker fits a personal lock and tag on every isolation point after switching off and testing for dead, so no one can re-energise the circuit until the last lock is removed
C.IEC 60479 places the onset of fibrillation near 30–50 mA for a few hundred milliseconds, which is why 30 mA residual-current protection is chosen for personnel
D.CEA Safety Regulations require every fatal or non-fatal electrical accident to be reported to the Electrical Inspector within 48 hours, followed by a detailed written report
Answer + AI explanation with Pro
17. Which term means: "Indian recommendations on safety procedures and practices in electrical work, Part 1 general and Part 2 life-saving techniques including rescue and artificial respiration"?
Junior
A.Working at height
B.IS 5216
C.Five safety rules
D.Arc flash PPE categories
Answer + AI explanation with Pro
18. Which statement is correct?
Junior
A.IS 5216 — Indian recommendations on safety procedures and practices in electrical work, Part 1 general and Part 2 life-saving techniques including rescue and artificial respiration
B.IS 5216 — isolate, secure against reconnection, verify dead with a tested detector, earth and short-circuit, then screen adjacent live parts, in that order before any work
C.IS 5216 — CEA schedule of minimum distances from exposed live parts for work: 2.6 m at 12 kV, 2.8 m at 36 kV, 3.1 m at 72.5 kV, 3.7 m at 145 kV, 4.3 m at 245 kV and 6.4 m at 420 kV
D.IS 5216 — each worker fits a personal lock and tag on every isolation point after switching off and testing for dead, so no one can re-energise the circuit until the last lock is removed
Answer + AI explanation with Pro
19. What is Safety working clearance?
Mid
A.formal authorisation by an issuer to a receiver listing the isolations, earths and safe zone, held live until the receiver returns it and the issuer cancels it before re-energisation
B.full-body harness with double lanyard anchored above about 1.8 m, ladders at a 4:1 slope, and no work near live overhead lines from ladders or structures without a permit and discharge
C.NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance
D.CEA schedule of minimum distances from exposed live parts for work: 2.6 m at 12 kV, 2.8 m at 36 kV, 3.1 m at 72.5 kV, 3.7 m at 145 kV, 4.3 m at 245 kV and 6.4 m at 420 kV
Answer + AI explanation with Pro
20. Which term means: "CEA schedule of minimum distances from exposed live parts for work: 2.6 m at 12 kV, 2.8 m at 36 kV, 3.1 m at 72.5 kV, 3.7 m at 145 kV, 4.3 m at 245 kV and 6.4 m at 420 kV"?
Mid
A.Five safety rules
B.Working at height
C.Safety working clearance
D.Arc flash PPE categories
Answer + AI explanation with Pro
21. Which statement is correct?
Mid
A.Safety working clearance — each worker fits a personal lock and tag on every isolation point after switching off and testing for dead, so no one can re-energise the circuit until the last lock is removed
B.Safety working clearance — formal authorisation by an issuer to a receiver listing the isolations, earths and safe zone, held live until the receiver returns it and the issuer cancels it before re-energisation
C.Safety working clearance — Indian recommendations on safety procedures and practices in electrical work, Part 1 general and Part 2 life-saving techniques including rescue and artificial respiration
D.Safety working clearance — CEA schedule of minimum distances from exposed live parts for work: 2.6 m at 12 kV, 2.8 m at 36 kV, 3.1 m at 72.5 kV, 3.7 m at 145 kV, 4.3 m at 245 kV and 6.4 m at 420 kV
Answer + AI explanation with Pro
22. What is Ventricular fibrillation threshold?
Junior
A.NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance
B.isolate, secure against reconnection, verify dead with a tested detector, earth and short-circuit, then screen adjacent live parts, in that order before any work
C.CEA schedule of minimum distances from exposed live parts for work: 2.6 m at 12 kV, 2.8 m at 36 kV, 3.1 m at 72.5 kV, 3.7 m at 145 kV, 4.3 m at 245 kV and 6.4 m at 420 kV
D.IEC 60479 places the onset of fibrillation near 30–50 mA for a few hundred milliseconds, which is why 30 mA residual-current protection is chosen for personnel
Answer + AI explanation with Pro
23. Which term means: "IEC 60479 places the onset of fibrillation near 30–50 mA for a few hundred milliseconds, which is why 30 mA residual-current protection is chosen for personnel"?
Junior
A.Ventricular fibrillation threshold
B.Safety working clearance
C.Electrical accident reporting
D.IS 5216
Answer + AI explanation with Pro
24. Which statement is correct?
Junior
A.Ventricular fibrillation threshold — CEA schedule of minimum distances from exposed live parts for work: 2.6 m at 12 kV, 2.8 m at 36 kV, 3.1 m at 72.5 kV, 3.7 m at 145 kV, 4.3 m at 245 kV and 6.4 m at 420 kV
B.Ventricular fibrillation threshold — CEA Safety Regulations require every fatal or non-fatal electrical accident to be reported to the Electrical Inspector within 48 hours, followed by a detailed written report
C.Ventricular fibrillation threshold — Indian recommendations on safety procedures and practices in electrical work, Part 1 general and Part 2 life-saving techniques including rescue and artificial respiration
D.Ventricular fibrillation threshold — IEC 60479 places the onset of fibrillation near 30–50 mA for a few hundred milliseconds, which is why 30 mA residual-current protection is chosen for personnel
Answer + AI explanation with Pro
25. What is Working at height?
Mid
A.NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance
B.CEA schedule of minimum distances from exposed live parts for work: 2.6 m at 12 kV, 2.8 m at 36 kV, 3.1 m at 72.5 kV, 3.7 m at 145 kV, 4.3 m at 245 kV and 6.4 m at 420 kV
C.CEA Safety Regulations require every fatal or non-fatal electrical accident to be reported to the Electrical Inspector within 48 hours, followed by a detailed written report
D.full-body harness with double lanyard anchored above about 1.8 m, ladders at a 4:1 slope, and no work near live overhead lines from ladders or structures without a permit and discharge
Answer + AI explanation with Pro
26. Which term means: "full-body harness with double lanyard anchored above about 1.8 m, ladders at a 4:1 slope, and no work near live overhead lines from ladders or structures without a permit and discharge"?
Mid
A.Lockout-tagout
B.Arc flash PPE categories
C.Permit-to-work
D.Working at height
Answer + AI explanation with Pro
27. Which statement is correct?
Mid
A.Working at height — NFPA 70E categories 1 to 4 correspond to arc ratings of 4, 8, 25 and 40 cal/cm², selected from the incident energy calculated at the working distance
B.Working at height — Indian recommendations on safety procedures and practices in electrical work, Part 1 general and Part 2 life-saving techniques including rescue and artificial respiration
C.Working at height — formal authorisation by an issuer to a receiver listing the isolations, earths and safe zone, held live until the receiver returns it and the issuer cancels it before re-energisation
D.Working at height — full-body harness with double lanyard anchored above about 1.8 m, ladders at a 4:1 slope, and no work near live overhead lines from ladders or structures without a permit and discharge
Answer + AI explanation with Pro