33 Protection & Switchgear questions from the Electrical Design bank, written for Indian campus drives and tech interviews. Every question has a verified answer and an AI-tutor explanation on placd.
Free to start: the 2-minute EE readiness check — six questions and a result.
A.voltage that appears across breaker contacts immediately after current interruption, which must stay below the breaker withstand to avoid re-strike
B.compares current entering and leaving a zone and trips on the difference, with a bias slope to restrain against CT mismatch on through-faults
C.arc is quenched in sulphur hexafluoride, whose dielectric strength is about 2.5 times air; standard at 66 kV and above despite being a potent greenhouse gas
D.overcurrent relay whose operating time falls as fault current rises, the IEC standard-inverse curve being t = 0.14·TMS/(I^0.02 − 1)
Answer + AI explanation with Pro
2. Which term means: "compares current entering and leaving a zone and trips on the difference, with a bias slope to restrain against CT mismatch on through-faults"?
Junior
A.IEC 61850 GOOSE
B.SF6 circuit breaker
C.Transient recovery voltage
D.Differential protection
Answer + AI explanation with Pro
3. Which statement is correct?
Junior
A.Differential protection — high-impedance differential scheme on a transformer winding that detects earth faults near the neutral which biased differential cannot see
B.Differential protection — interval of 0.2–0.4 s kept between successive IDMT relays to cover breaker operating time, relay overshoot and CT/relay errors
C.Differential protection — compares current entering and leaving a zone and trips on the difference, with a bias slope to restrain against CT mismatch on through-faults
D.Differential protection — gas-actuated relay in the pipe between tank and conservator that alarms on slow gas accumulation and trips on a sudden oil surge
Answer + AI explanation with Pro
4. What is SF6 circuit breaker?
Junior
A.interval of 0.2–0.4 s kept between successive IDMT relays to cover breaker operating time, relay overshoot and CT/relay errors
B.arc is quenched in sulphur hexafluoride, whose dielectric strength is about 2.5 times air; standard at 66 kV and above despite being a potent greenhouse gas
C.voltage that appears across breaker contacts immediately after current interruption, which must stay below the breaker withstand to avoid re-strike
D.protection CT with 5% composite error at 20 times rated current, unlike metering classes 0.2 or 0.5 that are accurate only near rated current
Answer + AI explanation with Pro
5. Which term means: "arc is quenched in sulphur hexafluoride, whose dielectric strength is about 2.5 times air; standard at 66 kV and above despite being a potent greenhouse gas"?
Junior
A.IDMT relay
B.Buchholz relay
C.SF6 circuit breaker
D.Distance relay zones
Answer + AI explanation with Pro
6. Which statement is correct?
Junior
A.SF6 circuit breaker — high-impedance differential scheme on a transformer winding that detects earth faults near the neutral which biased differential cannot see
B.SF6 circuit breaker — voltage that appears across breaker contacts immediately after current interruption, which must stay below the breaker withstand to avoid re-strike
C.SF6 circuit breaker — arc is quenched in sulphur hexafluoride, whose dielectric strength is about 2.5 times air; standard at 66 kV and above despite being a potent greenhouse gas
D.SF6 circuit breaker — protection CT with 5% composite error at 20 times rated current, unlike metering classes 0.2 or 0.5 that are accurate only near rated current
Answer + AI explanation with Pro
7. What is Vacuum circuit breaker?
Junior
A.contacts part inside a sealed vacuum interrupter and the arc dies at the first current zero; the dominant choice from 3.3 kV to 33 kV
B.arc is quenched in sulphur hexafluoride, whose dielectric strength is about 2.5 times air; standard at 66 kV and above despite being a potent greenhouse gas
C.voltage that appears across breaker contacts immediately after current interruption, which must stay below the breaker withstand to avoid re-strike
D.gas-actuated relay in the pipe between tank and conservator that alarms on slow gas accumulation and trips on a sudden oil surge
Answer + AI explanation with Pro
8. Which term means: "contacts part inside a sealed vacuum interrupter and the arc dies at the first current zero; the dominant choice from 3.3 kV to 33 kV"?
Junior
A.Grading margin
B.Vacuum circuit breaker
C.IEC 61850 GOOSE
D.Transient recovery voltage
Answer + AI explanation with Pro
9. Which statement is correct?
Junior
A.Vacuum circuit breaker — contacts part inside a sealed vacuum interrupter and the arc dies at the first current zero; the dominant choice from 3.3 kV to 33 kV
B.Vacuum circuit breaker — overcurrent relay whose operating time falls as fault current rises, the IEC standard-inverse curve being t = 0.14·TMS/(I^0.02 − 1)
C.Vacuum circuit breaker — interval of 0.2–0.4 s kept between successive IDMT relays to cover breaker operating time, relay overshoot and CT/relay errors
D.Vacuum circuit breaker — gas-actuated relay in the pipe between tank and conservator that alarms on slow gas accumulation and trips on a sudden oil surge
Answer + AI explanation with Pro
10. What is Buchholz relay?
Junior
A.arc is quenched in sulphur hexafluoride, whose dielectric strength is about 2.5 times air; standard at 66 kV and above despite being a potent greenhouse gas
B.gas-actuated relay in the pipe between tank and conservator that alarms on slow gas accumulation and trips on a sudden oil surge
C.interval of 0.2–0.4 s kept between successive IDMT relays to cover breaker operating time, relay overshoot and CT/relay errors
D.contacts part inside a sealed vacuum interrupter and the arc dies at the first current zero; the dominant choice from 3.3 kV to 33 kV
Answer + AI explanation with Pro
11. Which term means: "gas-actuated relay in the pipe between tank and conservator that alarms on slow gas accumulation and trips on a sudden oil surge"?
Junior
A.Buchholz relay
B.Differential protection
C.Grading margin
D.Transient recovery voltage
Answer + AI explanation with Pro
12. Which statement is correct?
Junior
A.Buchholz relay — high-impedance differential scheme on a transformer winding that detects earth faults near the neutral which biased differential cannot see
B.Buchholz relay — peer-to-peer Ethernet multicast message that carries trips and interlocks between IEDs within about 4 ms, replacing hard-wired copper links
C.Buchholz relay — compares current entering and leaving a zone and trips on the difference, with a bias slope to restrain against CT mismatch on through-faults
D.Buchholz relay — gas-actuated relay in the pipe between tank and conservator that alarms on slow gas accumulation and trips on a sudden oil surge
Answer + AI explanation with Pro
13. What is IDMT relay?
Mid
A.high-impedance differential scheme on a transformer winding that detects earth faults near the neutral which biased differential cannot see
B.overcurrent relay whose operating time falls as fault current rises, the IEC standard-inverse curve being t = 0.14·TMS/(I^0.02 − 1)
C.protection CT with 5% composite error at 20 times rated current, unlike metering classes 0.2 or 0.5 that are accurate only near rated current
D.contacts part inside a sealed vacuum interrupter and the arc dies at the first current zero; the dominant choice from 3.3 kV to 33 kV
Answer + AI explanation with Pro
14. Which term means: "overcurrent relay whose operating time falls as fault current rises, the IEC standard-inverse curve being t = 0.14·TMS/(I^0.02 − 1)"?
Mid
A.IEC 61850 GOOSE
B.Transient recovery voltage
C.Differential protection
D.IDMT relay
Answer + AI explanation with Pro
15. Which statement is correct?
Mid
A.IDMT relay — contacts part inside a sealed vacuum interrupter and the arc dies at the first current zero; the dominant choice from 3.3 kV to 33 kV
B.IDMT relay — interval of 0.2–0.4 s kept between successive IDMT relays to cover breaker operating time, relay overshoot and CT/relay errors
C.IDMT relay — arc is quenched in sulphur hexafluoride, whose dielectric strength is about 2.5 times air; standard at 66 kV and above despite being a potent greenhouse gas
D.IDMT relay — overcurrent relay whose operating time falls as fault current rises, the IEC standard-inverse curve being t = 0.14·TMS/(I^0.02 − 1)
Answer + AI explanation with Pro
16. What is Distance relay zones?
Mid
A.interval of 0.2–0.4 s kept between successive IDMT relays to cover breaker operating time, relay overshoot and CT/relay errors
B.Zone 1 covers about 80% of the line instantaneously, Zone 2 reaches 120% with 0.3–0.5 s delay, Zone 3 backs up the adjacent line
C.high-impedance differential scheme on a transformer winding that detects earth faults near the neutral which biased differential cannot see
D.arc is quenched in sulphur hexafluoride, whose dielectric strength is about 2.5 times air; standard at 66 kV and above despite being a potent greenhouse gas
Answer + AI explanation with Pro
17. Which term means: "Zone 1 covers about 80% of the line instantaneously, Zone 2 reaches 120% with 0.3–0.5 s delay, Zone 3 backs up the adjacent line"?
Mid
A.Grading margin
B.Distance relay zones
C.IEC 61850 GOOSE
D.Buchholz relay
Answer + AI explanation with Pro
18. Which statement is correct?
Mid
A.Distance relay zones — Zone 1 covers about 80% of the line instantaneously, Zone 2 reaches 120% with 0.3–0.5 s delay, Zone 3 backs up the adjacent line
B.Distance relay zones — voltage that appears across breaker contacts immediately after current interruption, which must stay below the breaker withstand to avoid re-strike
C.Distance relay zones — compares current entering and leaving a zone and trips on the difference, with a bias slope to restrain against CT mismatch on through-faults
D.Distance relay zones — protection CT with 5% composite error at 20 times rated current, unlike metering classes 0.2 or 0.5 that are accurate only near rated current
Answer + AI explanation with Pro
19. What is CT class 5P20?
Mid
A.overcurrent relay whose operating time falls as fault current rises, the IEC standard-inverse curve being t = 0.14·TMS/(I^0.02 − 1)
B.peer-to-peer Ethernet multicast message that carries trips and interlocks between IEDs within about 4 ms, replacing hard-wired copper links
C.compares current entering and leaving a zone and trips on the difference, with a bias slope to restrain against CT mismatch on through-faults
D.protection CT with 5% composite error at 20 times rated current, unlike metering classes 0.2 or 0.5 that are accurate only near rated current
Answer + AI explanation with Pro
20. Which term means: "protection CT with 5% composite error at 20 times rated current, unlike metering classes 0.2 or 0.5 that are accurate only near rated current"?
Mid
A.IDMT relay
B.Differential protection
C.CT class 5P20
D.Distance relay zones
Answer + AI explanation with Pro
21. Which statement is correct?
Mid
A.CT class 5P20 — gas-actuated relay in the pipe between tank and conservator that alarms on slow gas accumulation and trips on a sudden oil surge
B.CT class 5P20 — protection CT with 5% composite error at 20 times rated current, unlike metering classes 0.2 or 0.5 that are accurate only near rated current
C.CT class 5P20 — arc is quenched in sulphur hexafluoride, whose dielectric strength is about 2.5 times air; standard at 66 kV and above despite being a potent greenhouse gas
D.CT class 5P20 — Zone 1 covers about 80% of the line instantaneously, Zone 2 reaches 120% with 0.3–0.5 s delay, Zone 3 backs up the adjacent line
Answer + AI explanation with Pro
22. What is IEC 61850 GOOSE?
Mid
A.interval of 0.2–0.4 s kept between successive IDMT relays to cover breaker operating time, relay overshoot and CT/relay errors
B.peer-to-peer Ethernet multicast message that carries trips and interlocks between IEDs within about 4 ms, replacing hard-wired copper links
C.voltage that appears across breaker contacts immediately after current interruption, which must stay below the breaker withstand to avoid re-strike
D.contacts part inside a sealed vacuum interrupter and the arc dies at the first current zero; the dominant choice from 3.3 kV to 33 kV
Answer + AI explanation with Pro
23. Which term means: "peer-to-peer Ethernet multicast message that carries trips and interlocks between IEDs within about 4 ms, replacing hard-wired copper links"?
Mid
A.IEC 61850 GOOSE
B.Distance relay zones
C.SF6 circuit breaker
D.Buchholz relay
Answer + AI explanation with Pro
24. Which statement is correct?
Mid
A.IEC 61850 GOOSE — peer-to-peer Ethernet multicast message that carries trips and interlocks between IEDs within about 4 ms, replacing hard-wired copper links
B.IEC 61850 GOOSE — arc is quenched in sulphur hexafluoride, whose dielectric strength is about 2.5 times air; standard at 66 kV and above despite being a potent greenhouse gas
C.IEC 61850 GOOSE — overcurrent relay whose operating time falls as fault current rises, the IEC standard-inverse curve being t = 0.14·TMS/(I^0.02 − 1)
D.IEC 61850 GOOSE — Zone 1 covers about 80% of the line instantaneously, Zone 2 reaches 120% with 0.3–0.5 s delay, Zone 3 backs up the adjacent line
Answer + AI explanation with Pro
25. What is Transient recovery voltage?
Mid
A.peer-to-peer Ethernet multicast message that carries trips and interlocks between IEDs within about 4 ms, replacing hard-wired copper links
B.protection CT with 5% composite error at 20 times rated current, unlike metering classes 0.2 or 0.5 that are accurate only near rated current
C.interval of 0.2–0.4 s kept between successive IDMT relays to cover breaker operating time, relay overshoot and CT/relay errors
D.voltage that appears across breaker contacts immediately after current interruption, which must stay below the breaker withstand to avoid re-strike
Answer + AI explanation with Pro
26. Which term means: "voltage that appears across breaker contacts immediately after current interruption, which must stay below the breaker withstand to avoid re-strike"?
Mid
A.CT class 5P20
B.Transient recovery voltage
C.Distance relay zones
D.Vacuum circuit breaker
Answer + AI explanation with Pro
27. Which statement is correct?
Mid
A.Transient recovery voltage — gas-actuated relay in the pipe between tank and conservator that alarms on slow gas accumulation and trips on a sudden oil surge
B.Transient recovery voltage — voltage that appears across breaker contacts immediately after current interruption, which must stay below the breaker withstand to avoid re-strike
C.Transient recovery voltage — overcurrent relay whose operating time falls as fault current rises, the IEC standard-inverse curve being t = 0.14·TMS/(I^0.02 − 1)
D.Transient recovery voltage — compares current entering and leaving a zone and trips on the difference, with a bias slope to restrain against CT mismatch on through-faults
Answer + AI explanation with Pro
28. What is Grading margin?
Senior
A.peer-to-peer Ethernet multicast message that carries trips and interlocks between IEDs within about 4 ms, replacing hard-wired copper links
B.gas-actuated relay in the pipe between tank and conservator that alarms on slow gas accumulation and trips on a sudden oil surge
C.overcurrent relay whose operating time falls as fault current rises, the IEC standard-inverse curve being t = 0.14·TMS/(I^0.02 − 1)
D.interval of 0.2–0.4 s kept between successive IDMT relays to cover breaker operating time, relay overshoot and CT/relay errors
Answer + AI explanation with Pro
29. Which term means: "interval of 0.2–0.4 s kept between successive IDMT relays to cover breaker operating time, relay overshoot and CT/relay errors"?
Senior
A.SF6 circuit breaker
B.Grading margin
C.IEC 61850 GOOSE
D.Distance relay zones
Answer + AI explanation with Pro
30. Which statement is correct?
Senior
A.Grading margin — voltage that appears across breaker contacts immediately after current interruption, which must stay below the breaker withstand to avoid re-strike
B.Grading margin — interval of 0.2–0.4 s kept between successive IDMT relays to cover breaker operating time, relay overshoot and CT/relay errors
C.Grading margin — protection CT with 5% composite error at 20 times rated current, unlike metering classes 0.2 or 0.5 that are accurate only near rated current
D.Grading margin — arc is quenched in sulphur hexafluoride, whose dielectric strength is about 2.5 times air; standard at 66 kV and above despite being a potent greenhouse gas
Answer + AI explanation with Pro
Showing 30 of 33 Protection & Switchgear questions — the full set, with answers, explanations and an AI tutor on every question, is inside.
Free to start
Start with a free readiness check
Sign up free for the 2-minute EE readiness check and a scored result. Answers, explanations and the AI tutor on every Protection & Switchgear question come with Pro.