Renewable & Storage Design interview questions

33 Renewable & Storage Design questions from the Electrical Design bank, written for Indian campus drives and tech interviews. Every question has a verified answer and an AI-tutor explanation on placd.

Free to start: the 2-minute EE readiness check — six questions and a result.

Take the free EE readiness check

or take a mock interview set up for this area

1. What is IEC 61215 and IEC 61730?

Junior
  1. A.grid-code requirements that wind and solar plants ride through low and high voltage, provide reactive support and respond to frequency
  2. B.module design-qualification tests (thermal cycling, humidity-freeze, mechanical load) and module safety standard; ALMM listing is also mandatory for government projects
  3. C.inverter algorithm such as perturb-and-observe or incremental conductance that tracks the knee of the I-V curve where power peaks as irradiance changes
  4. D.Type 1 fixed-speed induction, Type 2 variable-slip wound rotor, Type 3 DFIG with about 30% partial converter, Type 4 full-converter synchronous

Answer + AI explanation with Pro

2. Which term means: "module design-qualification tests (thermal cycling, humidity-freeze, mechanical load) and module safety standard; ALMM listing is also mandatory for government projects"?

Junior
  1. A.MPPT
  2. B.CEA connectivity standards for RE
  3. C.Wind turbine types
  4. D.IEC 61215 and IEC 61730

Answer + AI explanation with Pro

3. Which statement is correct?

Junior
  1. A.IEC 61215 and IEC 61730 — module design-qualification tests (thermal cycling, humidity-freeze, mechanical load) and module safety standard; ALMM listing is also mandatory for government projects
  2. B.IEC 61215 and IEC 61730 — module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output
  3. C.IEC 61215 and IEC 61730 — inverter loading ratio of 1.2–1.4 oversizes the array to lift capacity utilisation, accepting clipping at peak irradiance
  4. D.IEC 61215 and IEC 61730 — string units up to a few hundred kW give granular MPPT and easy replacement; central 1–5 MW units give lower cost per watt for uniform utility arrays

Answer + AI explanation with Pro

4. What is MPPT?

Junior
  1. A.module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output
  2. B.module design-qualification tests (thermal cycling, humidity-freeze, mechanical load) and module safety standard; ALMM listing is also mandatory for government projects
  3. C.GHI is total on a horizontal plane, DNI the direct beam and DHI the diffuse part; most of India receives 4–7 kWh/m² per day
  4. D.inverter algorithm such as perturb-and-observe or incremental conductance that tracks the knee of the I-V curve where power peaks as irradiance changes

Answer + AI explanation with Pro

5. Which term means: "inverter algorithm such as perturb-and-observe or incremental conductance that tracks the knee of the I-V curve where power peaks as irradiance changes"?

Junior
  1. A.String vs central inverter
  2. B.MPPT
  3. C.String sizing
  4. D.Wind turbine types

Answer + AI explanation with Pro

6. Which statement is correct?

Junior
  1. A.MPPT — inverter loading ratio of 1.2–1.4 oversizes the array to lift capacity utilisation, accepting clipping at peak irradiance
  2. B.MPPT — Type 1 fixed-speed induction, Type 2 variable-slip wound rotor, Type 3 DFIG with about 30% partial converter, Type 4 full-converter synchronous
  3. C.MPPT — inverter algorithm such as perturb-and-observe or incremental conductance that tracks the knee of the I-V curve where power peaks as irradiance changes
  4. D.MPPT — GHI is total on a horizontal plane, DNI the direct beam and DHI the diffuse part; most of India receives 4–7 kWh/m² per day

Answer + AI explanation with Pro

7. What is Irradiance terms?

Junior
  1. A.GHI is total on a horizontal plane, DNI the direct beam and DHI the diffuse part; most of India receives 4–7 kWh/m² per day
  2. B.modules in series chosen so Voc at the coldest site temperature stays below the 1000/1500 V limit and Vmp at the hottest stays above MPPT minimum
  3. C.module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output
  4. D.inverter loading ratio of 1.2–1.4 oversizes the array to lift capacity utilisation, accepting clipping at peak irradiance

Answer + AI explanation with Pro

8. Which term means: "GHI is total on a horizontal plane, DNI the direct beam and DHI the diffuse part; most of India receives 4–7 kWh/m² per day"?

Junior
  1. A.String vs central inverter
  2. B.IEC 61215 and IEC 61730
  3. C.Wind turbine types
  4. D.Irradiance terms

Answer + AI explanation with Pro

9. Which statement is correct?

Junior
  1. A.Irradiance terms — Type 1 fixed-speed induction, Type 2 variable-slip wound rotor, Type 3 DFIG with about 30% partial converter, Type 4 full-converter synchronous
  2. B.Irradiance terms — module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output
  3. C.Irradiance terms — inverter loading ratio of 1.2–1.4 oversizes the array to lift capacity utilisation, accepting clipping at peak irradiance
  4. D.Irradiance terms — GHI is total on a horizontal plane, DNI the direct beam and DHI the diffuse part; most of India receives 4–7 kWh/m² per day

Answer + AI explanation with Pro

10. What is String sizing?

Mid
  1. A.Type 1 fixed-speed induction, Type 2 variable-slip wound rotor, Type 3 DFIG with about 30% partial converter, Type 4 full-converter synchronous
  2. B.grid-code requirements that wind and solar plants ride through low and high voltage, provide reactive support and respond to frequency
  3. C.module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output
  4. D.modules in series chosen so Voc at the coldest site temperature stays below the 1000/1500 V limit and Vmp at the hottest stays above MPPT minimum

Answer + AI explanation with Pro

11. Which term means: "modules in series chosen so Voc at the coldest site temperature stays below the 1000/1500 V limit and Vmp at the hottest stays above MPPT minimum"?

Mid
  1. A.DC/AC ratio
  2. B.MPPT
  3. C.String sizing
  4. D.Temperature coefficient

Answer + AI explanation with Pro

12. Which statement is correct?

Mid
  1. A.String sizing — grid-code requirements that wind and solar plants ride through low and high voltage, provide reactive support and respond to frequency
  2. B.String sizing — modules in series chosen so Voc at the coldest site temperature stays below the 1000/1500 V limit and Vmp at the hottest stays above MPPT minimum
  3. C.String sizing — module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output
  4. D.String sizing — module design-qualification tests (thermal cycling, humidity-freeze, mechanical load) and module safety standard; ALMM listing is also mandatory for government projects

Answer + AI explanation with Pro

13. What is String vs central inverter?

Mid
  1. A.string units up to a few hundred kW give granular MPPT and easy replacement; central 1–5 MW units give lower cost per watt for uniform utility arrays
  2. B.GHI is total on a horizontal plane, DNI the direct beam and DHI the diffuse part; most of India receives 4–7 kWh/m² per day
  3. C.energy equals load times duration over depth of discharge and round-trip efficiency; LFP cells allow 80–90% DoD over 4000-plus cycles
  4. D.Type 2 DC SPDs at array and inverter plus equipotential bonding of module frames per IEC 62305-3 and IEC 61643

Answer + AI explanation with Pro

14. Which term means: "string units up to a few hundred kW give granular MPPT and easy replacement; central 1–5 MW units give lower cost per watt for uniform utility arrays"?

Mid
  1. A.DC/AC ratio
  2. B.String vs central inverter
  3. C.PV surge protection
  4. D.CEA connectivity standards for RE

Answer + AI explanation with Pro

15. Which statement is correct?

Mid
  1. A.String vs central inverter — string units up to a few hundred kW give granular MPPT and easy replacement; central 1–5 MW units give lower cost per watt for uniform utility arrays
  2. B.String vs central inverter — GHI is total on a horizontal plane, DNI the direct beam and DHI the diffuse part; most of India receives 4–7 kWh/m² per day
  3. C.String vs central inverter — module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output
  4. D.String vs central inverter — energy equals load times duration over depth of discharge and round-trip efficiency; LFP cells allow 80–90% DoD over 4000-plus cycles

Answer + AI explanation with Pro

16. What is DC/AC ratio?

Mid
  1. A.Type 2 DC SPDs at array and inverter plus equipotential bonding of module frames per IEC 62305-3 and IEC 61643
  2. B.Type 1 fixed-speed induction, Type 2 variable-slip wound rotor, Type 3 DFIG with about 30% partial converter, Type 4 full-converter synchronous
  3. C.modules in series chosen so Voc at the coldest site temperature stays below the 1000/1500 V limit and Vmp at the hottest stays above MPPT minimum
  4. D.inverter loading ratio of 1.2–1.4 oversizes the array to lift capacity utilisation, accepting clipping at peak irradiance

Answer + AI explanation with Pro

17. Which term means: "inverter loading ratio of 1.2–1.4 oversizes the array to lift capacity utilisation, accepting clipping at peak irradiance"?

Mid
  1. A.Wind turbine types
  2. B.BESS sizing
  3. C.DC/AC ratio
  4. D.CEA connectivity standards for RE

Answer + AI explanation with Pro

18. Which statement is correct?

Mid
  1. A.DC/AC ratio — modules in series chosen so Voc at the coldest site temperature stays below the 1000/1500 V limit and Vmp at the hottest stays above MPPT minimum
  2. B.DC/AC ratio — inverter algorithm such as perturb-and-observe or incremental conductance that tracks the knee of the I-V curve where power peaks as irradiance changes
  3. C.DC/AC ratio — inverter loading ratio of 1.2–1.4 oversizes the array to lift capacity utilisation, accepting clipping at peak irradiance
  4. D.DC/AC ratio — grid-code requirements that wind and solar plants ride through low and high voltage, provide reactive support and respond to frequency

Answer + AI explanation with Pro

19. What is Temperature coefficient?

Mid
  1. A.module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output
  2. B.modules in series chosen so Voc at the coldest site temperature stays below the 1000/1500 V limit and Vmp at the hottest stays above MPPT minimum
  3. C.string units up to a few hundred kW give granular MPPT and easy replacement; central 1–5 MW units give lower cost per watt for uniform utility arrays
  4. D.inverter loading ratio of 1.2–1.4 oversizes the array to lift capacity utilisation, accepting clipping at peak irradiance

Answer + AI explanation with Pro

20. Which term means: "module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output"?

Mid
  1. A.BESS sizing
  2. B.String sizing
  3. C.Wind turbine types
  4. D.Temperature coefficient

Answer + AI explanation with Pro

21. Which statement is correct?

Mid
  1. A.Temperature coefficient — energy equals load times duration over depth of discharge and round-trip efficiency; LFP cells allow 80–90% DoD over 4000-plus cycles
  2. B.Temperature coefficient — module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output
  3. C.Temperature coefficient — string units up to a few hundred kW give granular MPPT and easy replacement; central 1–5 MW units give lower cost per watt for uniform utility arrays
  4. D.Temperature coefficient — inverter algorithm such as perturb-and-observe or incremental conductance that tracks the knee of the I-V curve where power peaks as irradiance changes

Answer + AI explanation with Pro

22. What is BESS sizing?

Mid
  1. A.GHI is total on a horizontal plane, DNI the direct beam and DHI the diffuse part; most of India receives 4–7 kWh/m² per day
  2. B.inverter algorithm such as perturb-and-observe or incremental conductance that tracks the knee of the I-V curve where power peaks as irradiance changes
  3. C.grid-code requirements that wind and solar plants ride through low and high voltage, provide reactive support and respond to frequency
  4. D.energy equals load times duration over depth of discharge and round-trip efficiency; LFP cells allow 80–90% DoD over 4000-plus cycles

Answer + AI explanation with Pro

23. Which term means: "energy equals load times duration over depth of discharge and round-trip efficiency; LFP cells allow 80–90% DoD over 4000-plus cycles"?

Mid
  1. A.String sizing
  2. B.String vs central inverter
  3. C.BESS sizing
  4. D.PV surge protection

Answer + AI explanation with Pro

24. Which statement is correct?

Mid
  1. A.BESS sizing — Type 2 DC SPDs at array and inverter plus equipotential bonding of module frames per IEC 62305-3 and IEC 61643
  2. B.BESS sizing — Type 1 fixed-speed induction, Type 2 variable-slip wound rotor, Type 3 DFIG with about 30% partial converter, Type 4 full-converter synchronous
  3. C.BESS sizing — energy equals load times duration over depth of discharge and round-trip efficiency; LFP cells allow 80–90% DoD over 4000-plus cycles
  4. D.BESS sizing — GHI is total on a horizontal plane, DNI the direct beam and DHI the diffuse part; most of India receives 4–7 kWh/m² per day

Answer + AI explanation with Pro

25. What is PV surge protection?

Mid
  1. A.Type 2 DC SPDs at array and inverter plus equipotential bonding of module frames per IEC 62305-3 and IEC 61643
  2. B.modules in series chosen so Voc at the coldest site temperature stays below the 1000/1500 V limit and Vmp at the hottest stays above MPPT minimum
  3. C.module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output
  4. D.inverter algorithm such as perturb-and-observe or incremental conductance that tracks the knee of the I-V curve where power peaks as irradiance changes

Answer + AI explanation with Pro

26. Which term means: "Type 2 DC SPDs at array and inverter plus equipotential bonding of module frames per IEC 62305-3 and IEC 61643"?

Mid
  1. A.DC/AC ratio
  2. B.Wind turbine types
  3. C.String vs central inverter
  4. D.PV surge protection

Answer + AI explanation with Pro

27. Which statement is correct?

Mid
  1. A.PV surge protection — modules in series chosen so Voc at the coldest site temperature stays below the 1000/1500 V limit and Vmp at the hottest stays above MPPT minimum
  2. B.PV surge protection — Type 2 DC SPDs at array and inverter plus equipotential bonding of module frames per IEC 62305-3 and IEC 61643
  3. C.PV surge protection — string units up to a few hundred kW give granular MPPT and easy replacement; central 1–5 MW units give lower cost per watt for uniform utility arrays
  4. D.PV surge protection — inverter algorithm such as perturb-and-observe or incremental conductance that tracks the knee of the I-V curve where power peaks as irradiance changes

Answer + AI explanation with Pro

28. What is CEA connectivity standards for RE?

Senior
  1. A.modules in series chosen so Voc at the coldest site temperature stays below the 1000/1500 V limit and Vmp at the hottest stays above MPPT minimum
  2. B.grid-code requirements that wind and solar plants ride through low and high voltage, provide reactive support and respond to frequency
  3. C.inverter loading ratio of 1.2–1.4 oversizes the array to lift capacity utilisation, accepting clipping at peak irradiance
  4. D.Type 1 fixed-speed induction, Type 2 variable-slip wound rotor, Type 3 DFIG with about 30% partial converter, Type 4 full-converter synchronous

Answer + AI explanation with Pro

29. Which term means: "grid-code requirements that wind and solar plants ride through low and high voltage, provide reactive support and respond to frequency"?

Senior
  1. A.Temperature coefficient
  2. B.CEA connectivity standards for RE
  3. C.String vs central inverter
  4. D.PV surge protection

Answer + AI explanation with Pro

30. Which statement is correct?

Senior
  1. A.CEA connectivity standards for RE — string units up to a few hundred kW give granular MPPT and easy replacement; central 1–5 MW units give lower cost per watt for uniform utility arrays
  2. B.CEA connectivity standards for RE — module power falls about 0.3–0.4% per °C above the 25 °C STC cell temperature, so a 60 °C cell loses 12–14% output
  3. C.CEA connectivity standards for RE — grid-code requirements that wind and solar plants ride through low and high voltage, provide reactive support and respond to frequency
  4. D.CEA connectivity standards for RE — Type 1 fixed-speed induction, Type 2 variable-slip wound rotor, Type 3 DFIG with about 30% partial converter, Type 4 full-converter synchronous

Answer + AI explanation with Pro

Showing 30 of 33 Renewable & Storage Design questions — the full set, with answers, explanations and an AI tutor on every question, is inside.

Free to start

Start with a free readiness check

Sign up free for the 2-minute EE readiness check and a scored result. Answers, explanations and the AI tutor on every Renewable & Storage Design question come with Pro.

Take the free EE readiness check

or take a mock interview set up for this area

24,000+ questions & coding problemsSoftware & IT16,274 questionsGovernment jobs26 examsAptitudenew questions every timeAI practice interviewwith feedback65 topics to practiseMechanical1,149 questionsGATE ME9 papersEngineering Mathematics381 questions2-minute checkfreeDSA Problems1,422Civil1,005 questionsGATE CE9 papersCS Fundamentals1,209 questionsYour scores6 skillsSystem Design25Electrical / EEE1,047 questionsGATE EE9 papersRun your codeC++ · Java · PythonLow-Level Design144Electronics & Comm.975 questionsGATE EC9 papersAI help on every questionFull-Stack6,282Chemical1,005 questionsGATE CH9 papersAI whiteboardsystem designWork abroadEurope · remote · transfersESE ME1 paperGATE practice papers2019–2026ESE CE1 paperDate alertsbefore the last dateESE EE1 paperBehavioural courseHR round practiceESE ET1 paperResume optimizerProSSC JE ME1 paperApplication trackerSSC JE CE1 paperCompany-wise prepSSC JE EE1 paperRole roadmapsRRB JE1 subjectPriced in ₹UPI · cardsISRO SC1 paperGATE CS9 papersIBPS SO IT1 paperUGC NET CS1 paperSSC CGL26 papersIBPS PO26 papersRRB NTPC26 papersSSC CHSL26 papersIBPS Clerk26 papersSBI Clerk26 papersRRB Group D26 papersSSC CPO26 papersSSC GD26 papers